Ring Video Doorbell
Browse posts, comment, and join in the discussion about Rings wired and battery doorbell.
Ring Transformer delivering 30 volts
Installed Ring Pro doorbell and the health says danger and 30 volts getting to device.I have connected the transformer to the 16-24 volt connections. How can this be?
1773 •
0 •
0 •
15-04-2021 13:55:32
Responses (2)
- H
Spoke to electrician and he says a 24 AC transformer under limited load would more than likely register 30 V. The 24 AC rating is based on a given load, higher than a doorbell in standby. The electrician says theres nothing wrong with the transformer.
•0
16-04-2021 15:45:06
- H
Hi Scott,Thanks for the response. The transformer is branded Ring and is rated 16-24 VAC and 30VA.I will replace it.
•0
15-04-2021 21:55:49
•
Didn't find an answer ?
Log in or create your Ring account to post a question and join in the on the conversation.
Community Resources
Most Helpful Members
View All
©2024 Ring LLC or its affiliates
Scott_H
Check the specifications of the transformer. Make sure it's rated 16-24VAC preferably 30 or 40VA. Did you install the Pro Power kit that came with the doorbell? It's only required if you have a standard doorbell chime, but it's also recommended to install without a chime as it helps to balance voltage overall. If the transformer label is within this range, however it is outputting 30VAC under the load the doorbell draws, then it's likely a defective transformer. Replace it.